A quick question on bathroom earth bonding if I may.
I'm in the process of refitting the bathroom, and all being well will replace the bath this week. Originally the plumbing was all in copper, and there is a steel bath. The plumbing is being replaced with plastic (*), and the new bath is acrylic. Since there is there is very little in the way of metal, do I have to bond it. (*) the shower will have metal plumbing where visible (plastic where not), but is driven from the boiler (i.e. is non-electric). Adrian -- To Reply : replace "news" with "adrian" and "nospam" with "ffoil" Sorry for the rigmarole, If I want spam, I'll go to the shops Every time someone says "I don't believe in trolls", another one dies. |
#2
![]() |
|||
|
|||
![]()
In message ,
Adrian Simpson wrote: A quick question on bathroom earth bonding if I may. I'm in the process of refitting the bathroom, and all being well will replace the bath this week. Originally the plumbing was all in copper, and there is a steel bath. The plumbing is being replaced with plastic (*), and the new bath is acrylic. Since there is there is very little in the way of metal, do I have to bond it. (*) the shower will have metal plumbing where visible (plastic where not), but is driven from the boiler (i.e. is non-electric). If everything is plastic then there's not usually a requirement to bond radiators, taps and the like, however short lengths of plastic do not count as the water might be conductive enough to "bridge" the gap - there was a discussion on here about that a few months ago, but I can't remember what length of plastic before metal was determined to be "safe", something more than a couple of feet IIRC. It *is* a requirement to supplementary bond the protective conductors of electrical equipment within the zones, at least as far as the cord outlet - where something like a heater is supplied through a cord. See the On Site Guide Figures 4d and 4e, pages 30 and 31. Paragraph 4.7 on p26 is relevant and, assuming you do not have an OSG to hand here it is: "Supplementary bonding is not required to metal parts supplied by plastic pipes, such as metal hot and cold water taps supplied from plastic pipes. A metal bath not connected to extraneous-conductive parts (such as structural steelwork) with plastic hot and cold water pipes and plastic waste pipes does not require supplementary bonding. Supplementary bonding in a bathroom or shower room will still be required between the protective conductors of circuits supplying Class I and Class II equipment in the zones e.g. heaters, showers and accessible luminaires, see Figure 4e." HTH Hwyl! M. -- Martin Angove: http://www.tridwr.demon.co.uk/ Two free issues: http://www.livtech.co.uk/ Living With Technology .... Starkle Starkle Little Twink What the hell you are I think? |
#3
![]() |
|||
|
|||
![]()
and the new bath is acrylic. Since there is there is very little
in the way of metal, do I have to bond it. No. You wouldn't even bond a metal bath if the pipework is all plastic. Same with radiators/towel rails. Don't bond unless supplied by metallic pipe (or connected to structural metalwork/other possibly earthed item - very unlikely in domestic building). (*) the shower will have metal plumbing where visible (plastic where not), but is driven from the boiler (i.e. is non-electric). Basically, if the plastic supply length is greater than 1m and the metal plumbing doesn't go where it might get earthed accidentally by something, then it doesn't need bonding. 10cm of chrome where it goes into the wall to continue thence in plastic, I wouldn't bond. This isn't a case of laziness. It is SAFER not to bond in those specific circumstances. Christian. |
#4
![]() |
|||
|
|||
![]() "Adrian Simpson" wrote in message ... A quick question on bathroom earth bonding if I may. I'm in the process of refitting the bathroom, and all being well will replace the bath this week. Originally the plumbing was all in copper, and there is a steel bath. The plumbing is being replaced with plastic (*), and the new bath is acrylic. Since there is there is very little in the way of metal, do I have to bond it. No .. and to do so could make it less safe. There is a very good guide to bonding for plastic pipe installations on the Hepworth web site. Rick |
#5
![]() |
|||
|
|||
![]()
In article , Christian
McArdle writes and the new bath is acrylic. Since there is there is very little in the way of metal, do I have to bond it. No. You wouldn't even bond a metal bath if the pipework is all plastic. Same with radiators/towel rails. Don't bond unless supplied by metallic pipe (or connected to structural metalwork/other possibly earthed item - very unlikely in domestic building). OK, thanks for that. (*) the shower will have metal plumbing where visible (plastic where not), but is driven from the boiler (i.e. is non-electric). Basically, if the plastic supply length is greater than 1m and the metal plumbing doesn't go where it might get earthed accidentally by something, then it doesn't need bonding. 10cm of chrome where it goes into the wall to continue thence in plastic, I wouldn't bond. This isn't a case of laziness. It is SAFER not to bond in those specific circumstances. We are probably talking nearer a metre of chrome. Thanks also to Martin for his contribution. Adrian -- To Reply : replace "news" with "adrian" and "nospam" with "ffoil" Sorry for the rigmarole, If I want spam, I'll go to the shops Every time someone says "I don't believe in trolls", another one dies. |
#6
![]() |
|||
|
|||
![]()
In article , Adrian Simpson
writes A quick question on bathroom earth bonding if I may. I'm in the process of refitting the bathroom, and all being well will replace the bath this week. Originally the plumbing was all in copper, and there is a steel bath. The plumbing is being replaced with plastic (*), and the new bath is acrylic. Since there is there is very little in the way of metal, do I have to bond it. (*) the shower will have metal plumbing where visible (plastic where not), but is driven from the boiler (i.e. is non-electric). Adrian All electrical fittings must be supplementary bonded with extraneous conductive parts. That is light, shower, radiator, bath taps, bath (if connected to ground eg via lead waste pipe), basin taps, basin (if metallic eg stainless steel and connected to ground via for instance lead waste pipe) must all be connected with one continuous earth cable which should NOT be connected to the earthing terminal. See Http://www.iee.org/Publish/WireRegs/...asticPipes.pdf peruse the rest of the site. -- Z Remove all Zeds in e-mail address to reply. |
#7
![]() |
|||
|
|||
![]() "Z" wrote in message ... In article , Adrian Simpson writes All electrical fittings must be supplementary bonded with extraneous conductive parts. That is light, shower, radiator, bath taps, bath (if connected to ground eg via lead waste pipe), basin taps, basin (if metallic eg stainless steel and connected to ground via for instance lead waste pipe) must all be connected with one continuous earth cable which should NOT be connected to the earthing terminal. See Http://www.iee.org/Publish/WireRegs/...asticPipes.pdf peruse the rest of the site. Quite the opposite is true for metal waste pipes that come into contact with the ground. They must be main bonded back to the main earthing terminal. Also the IEE say that a metal bath should also be bonded even when metal pipes are used. -- Adam |
#8
![]() |
|||
|
|||
![]() "Z" wrote in message ... In article , Adrian Simpson writes A quick question on bathroom earth bonding if I may. I'm in the process of refitting the bathroom, and all being well will replace the bath this week. Originally the plumbing was all in copper, and there is a steel bath. The plumbing is being replaced with plastic (*), and the new bath is acrylic. Since there is there is very little in the way of metal, do I have to bond it. (*) the shower will have metal plumbing where visible (plastic where not), but is driven from the boiler (i.e. is non-electric). Adrian All electrical fittings must be supplementary bonded with extraneous conductive parts. That is light, shower, radiator, bath taps, bath (if connected to ground eg via lead waste pipe), basin taps, basin (if metallic eg stainless steel and connected to ground via for instance lead waste pipe) must all be connected with one continuous earth cable which should NOT be connected to the earthing terminal. Electrical fittings yes .. but taps & wastes - no. The IEE article I have on this system that supplementary bonding must NOT be done when plumbed out in plastic, and to do so could make it dangerous. I quote "... short lengths of metal pipework supplied by plastic pipes or metal taps connected to plastic pipes, metal baths supplied by plastic pipes and with a plastic waste do not require supplementary bonding." Text of the report is as follows : Earthing Plastic Pipes by Paul Cook of the Institute of Electrical Engineers You do not have to earth plastic pipes Plastic pipes make for a safer electrical installation and reduce the need for earthing. Festooning an installation that has been plumbed in plastic pipe with green and yellow earth wire is not necessary and of likely to reduce the level of electrical safety of the property, not increase it. Everyone knows that water and electricity do not mix, that the risk of electric shock is greater when there is water around. They know that the risk and severity of an electric shock is increased as a result of the presence of water. This may be the reason for the concern that water In plastic pipes may conduct electricity and that bonding is required. Because of this, the IEE commissioned the Electrical Research Association to carry out measurements of the electrical conductivity of water in plastic pipes. The ERA tests confirm that tap water in a plastic pipe is a poor conductor of electricity. One metre of 15mm diameter of plastic pipe filled with tap water from Leatherhead where the ERA are based, has resistance of 100,000 Ohms. This one metre of 15mm pipe will restrict currents to less than fatal values and of course in practice, there would be many metres of pipe between metal items of plumbing equipment and earth. The resistance of water varies around the country, it is reduced by impurities, not all of which are harmful. The additives put into water of central heating systems to reduce corrosion make the most difference, as can be seen from the table below. Resistance - Ohms 15mm diameter, tap water 115.000 20mm diameter, tap water 65,000 15mm diameter, tap water with double dose of inhibitor at 60°C 20,200 So why do wet hands and immersion in a bath increase the risk of electric shock? The human body plus clothes, particularly shoes has an impedance of about 3,000 Ohms - see next table. At 230 volts this will result in a current of about 153mA (153 thousandths of an amp). This is not nice, but is unlikely to kill you. If there are no shoes and hands are wet, the impedance falls to 500 Ohms and the current at 230 volts is 460mA. This is getting decidedly unpleasant. Immersion of the body in a bath, in effect halves the impedance of the body and current at 230 volts would be then 1,000 mA. This is dangerous, and can kill. Siliation Body Impedance Current at 230 V Dry with shoes3000 + Ohms 76 mA Dry 1500 Ohms 153 mA Wet 500 Ohms 460 mA Body 1/2 immersed250 Ohms 920 mA Horny dry hands and feet are quite good insulation. However, if the hands are wet, salts and contaminants improve the contact and reduce the resistance of the skin. Dry skin has a high resistance, wet skin has a relatively low resistance. The other reason why bathrooms and such places are relatively risky electrically, is the presence of earthed metal. Should you be unfortunate enough to touch the lie parts of broken equipment and nothing else except say a well insulated floor, there would be little result. Electrical jointers and fitters regularly work live under such controlled conditions. However if you touch a live part and an earthed metal pipe, then you get a very dangerous electric shock. An earthly environment where there are lots of metal pipes is potentially less safe than an earth free environment. We can now start to see why plastic pipe installations are going to lead to safer installations. For a start, there is not all that earthed metal around. The bonding requirements for plastic piped and metal pipes installations is described below. At the Service Position - Main Bonding In each electrical installation, main equipotential bonding conductors (earthing wires) are required to connect to the main earthing terminal for the installation of the following: metal water service pipes metal gas installation pipes other metal service pipes and ducting metal central heating and air conditioning systems exposed metal structural parts of the building lightning protection systems It is important to note that the reference above is always to metal pipes. If the pipes are made of plastic, they do not need to be main bonded. If the incoming pipes are made of plastic, but the pipes within the electrical installation are made of metal, the main bonding must be carried out. The bonding being applied on the customer side of any meter, main stopcock or insulating insert and of course to the metal pipes of the installation. The connections of the bonding wired to the pipes has to be made with a proper clamp to BS 951 complete with the label "SAFETY OF ELECTRICAL CONNECTION - DO NOT REMOVE." If the incoming services are made of plastic and the pipework within the building is of plastic then no main bonding is required. If some of the services are of metal and some are plastic, then those that are of metal must be main bonded. In the bathroom - Supplementary Binding Supplementary or additional equipotential bonding (earthing) is required in locations of increased shock risk. In domestic premises the locations identified as having this increased shock risk are rooms containing a bath or shower (bathrooms) and if you are lucky to have one, in the areas surrounding swimming pools. Please note, there is no specific requirement to carry our supplementary bonding domestic kitchens, wash rooms and lavatories test do not have a bath or shower. That is not to say that supplementary bonding in a kitchen or wash room is wrong (it would be wrong for plastic pipes!) but it is not necessary. For plastic pipe installation within a bathroom the plastic pipes do not require supplementary bonding and metal fitments attached to these plastic pipes also would not require supplementary bonding. It seems to to be the practice of some builders to effect all the plumbing in plastic except for those bits of the pipework that are visible. These short lengths of metal pipework supplied by plastic pipes or metal taps connected to plastic pipes, metal baths supplied by plastic pipes and with a plastic waste do not require supplementary bonding. However, electrical equipment still does require to be supplementary bonded and if an electric shower, or radiant heater is fitted, they will require to be supplementary bonded as usual. This requirement does not apply to class II or all insulated equipment where no metal work that is likely to become alive in the event of a fault, is accessible. However, it is recommended that supplementary bonds are run to the earth terminals of all electrical equipment accessories e.g. flex outlets, or the equipment itself, as class II equipment may be replaced by class I during the life of the installation. General on Supplementary Bonding for bathrooms: Metal radiators supplied by plastic pipes should not be supplementary bonded. It is safer not to supplementary bond them. Locations generally are safer if the location is earth free as discussed earlier. Metal (class I) items of equipment (e.g. electrical heaters and showers) require supplementary bonding if simultaneously accessible. Supplementary bonds to be connected to the protective conductors of each circuit at the accessory point. Supplementary bonding of short lengths of copper pipe (less than 0.5m in length) installed where the pipes are visible, is not necessary. Supplementary Bonding is carried out to the earth terminal of equipment within the bathroom with exposed-conductive part. A supplementary bond is not run back to the main earth Metal window frames are not required to be supplementary bonded unless they are electrically connected to the metallic structure of the building Metal baths are supplied by metal pipes do not require supplementary bonding if all the pipes are bonded and there is no other connection of the bath to earth. All bonding connections must be accessible and labelled "Safety Electrical Connection - Do Not Remove". The full article with diagrams is available from Hepworths at: http://www.hepworthbp.co.uk/Pages/Hep20frame.htm click on the link to earth Bonding |
#9
![]() |
|||
|
|||
![]()
In article ,
ARWadsworth writes "Z" wrote in message ... In article , Adrian Simpson writes All electrical fittings must be supplementary bonded with extraneous conductive parts. That is light, shower, radiator, bath taps, bath (if connected to ground eg via lead waste pipe), basin taps, basin (if metallic eg stainless steel and connected to ground via for instance lead waste pipe) must all be connected with one continuous earth cable which should NOT be connected to the earthing terminal. See Http://www.iee.org/Publish/WireRegs/...asticPipes.pdf peruse the rest of the site. Quite the opposite is true for metal waste pipes that come into contact with the ground. They must be main bonded back to the main earthing terminal. Also the IEE say that a metal bath should also be bonded even when metal pipes are used. Please be careful in snipping, I didn't write any of the above, but the attributes imply that I did. I'll have a look at the IEE site when I get half an hour or so (not tonight !). Currently the only electrical fittings in the bathroom are the main light (which is earthed in the usual way), the light switch (ditto) and the switch for the fan (ditto). The fan itself is mounted in the loft, so I would not regard that as a bathroom fitting. In due course, I expect to fit a light/shaver socket in proximity to the sink, which I would expect to earth via the T&E cable supplying it. The waste pipes are all plastic, heating is via a central heating radiator (copper piping), and the sanitary ware will be either plastic or ceramic. This leaves the shower which has a metal mixer valve and visible pipe work ,otherwise it is plastic. Thanks Adrian -- To Reply : replace "news" with "adrian" and "nospam" with "ffoil" Sorry for the rigmarole, If I want spam, I'll go to the shops Every time someone says "I don't believe in trolls", another one dies. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
![]() |
||||
Thread | Forum | |||
Earth bonding queries | UK diy | |||
Generator Grounding | UK diy | |||
Ceiling fan earth | UK diy | |||
simple earth checking? | UK diy | |||
How to find earth | UK diy |