consumer unit location
That's where I'm lucky - moving the CU to where I want to makes it
closer to the metre than it is at the moment - have to move the tails
but that shouldn't be too hard.
Thanks for all the replies
Mark
"Lurch" wrote in message
...
On Tue, 17 Feb 2004 09:57:44 -0000, "Christian McArdle"
wrote:
Thanks, that was what I was hoping for, makes life so much easier.
However, there could be a problem. It is not usually allowed to have the
meter tails more than 2 metres long, as the supplier doesn't like
protecting
part of your installation with their service fuse. If you need to have
longer tails than this you need to install a switchfuse unit next to the
meter with a suitable fuse (i.e. 60A or 100A, whatever your supply is
rated
for). A fuse is better than an MCB for this, as you don't really want it
to
blow before the circuit MCBs get a chance.
Go on then. In theory though you can get away with a bit more, I
usually go on about 3m or just over. If you're going over this
distance I would usually use a MEM 800KMF, (ask at your local
wholesaler), with a 80A fuse on 25mm tails.
..
SJW